GFCI (= RCBO) trips when connected to online UPS
Posted: Wed May 06, 2020 8:42 pm
@all,
@timkb4cq,
@m_pav,
@JayM,
@figueroa:
I am currently testing a rarely used, rather new, high quality 2000 VA online (= double conversion) (https://en.wikipedia.org/wiki/Uninterru ... conversion) Uninterruptible Power Supply (UPS) (https://en.wikipedia.org/wiki/Uninterru ... wer_supply), which, according to its boot-up self-test, battery voltage and overall behavior seems to be fully intact.
The problem I am experiencing is that it makes the central GFCI (also known as RCBO, cf. https://en.wikipedia.org/wiki/Residual- ... I_breaker), which is located before the UPS, trip every now and then.
The GFCI (= RCBO) is to trip when earth leakage is above 30 mA and/or current exceeds 40 A.
My first thought that the UPS's filtering mechanism was adding to much earth leakage to the overall earth leakage sum generated by other appliances (to my knowledge, many appliances have about 3 mA of earth leage in standard operation). Hence I installed a second, discrete GFCI (= RCBO) only for the office room the UPS was in, and tested the UPS with no other appliances running. However, even with that second test configuration, that (second) GFCI (= RCBO) trips every now and then.
Any idea what's going on here?
The GFCI (= RCBO) model used is a high-quality double-pole one.
According to its specs, the UPS is to deliver pure sine wave.
Interesting observation is that tripping occurs even when not even a single appliance is connected to the UPS.
Thanks in advance for any hint
, Joe
@timkb4cq,
@m_pav,
@JayM,
@figueroa:
I am currently testing a rarely used, rather new, high quality 2000 VA online (= double conversion) (https://en.wikipedia.org/wiki/Uninterru ... conversion) Uninterruptible Power Supply (UPS) (https://en.wikipedia.org/wiki/Uninterru ... wer_supply), which, according to its boot-up self-test, battery voltage and overall behavior seems to be fully intact.
The problem I am experiencing is that it makes the central GFCI (also known as RCBO, cf. https://en.wikipedia.org/wiki/Residual- ... I_breaker), which is located before the UPS, trip every now and then.
The GFCI (= RCBO) is to trip when earth leakage is above 30 mA and/or current exceeds 40 A.
My first thought that the UPS's filtering mechanism was adding to much earth leakage to the overall earth leakage sum generated by other appliances (to my knowledge, many appliances have about 3 mA of earth leage in standard operation). Hence I installed a second, discrete GFCI (= RCBO) only for the office room the UPS was in, and tested the UPS with no other appliances running. However, even with that second test configuration, that (second) GFCI (= RCBO) trips every now and then.
Any idea what's going on here?
The GFCI (= RCBO) model used is a high-quality double-pole one.
According to its specs, the UPS is to deliver pure sine wave.
Interesting observation is that tripping occurs even when not even a single appliance is connected to the UPS.
Thanks in advance for any hint